Clean drawing. I like the ability to use CCP2 as a backup source for your 12v loads (assuming that's what is indicated by "12v fuses". Couple of questions/thoughts:
1) What are the hall effect sensors on your + battery connections for?
2) are you planning any disconnecting means or fuse protection on the individual batteries?
3) why two series 75a breakers in series on the solar input? I'm unfamiliar with the Midnight solar charge controller
4) are you planning on grounding the -DC bus to the vehicle chassis? You'll probably need to if your loads are counting on it as a reference, specifically if you're powering them from CCP2
5) assuming no battery fuses (see #2) make sure that 150a breaker between your + DC bus and the 120a DCDC can interrupt a maximum fault current from the batteries.
6) consider an ELCI on the shore power inlet.